Garage Wiring Query
Hi, I have a detached double garage to my new build which has power running to it from a 20A MCB (protected by an RCD) in the house Consumer Unit, which connects to a second CU in the garage. The garage CU contains a 6A MCB for the garage light and a 16A MCB for the double socket. Would I be able to uprate the 16A MCB to a 20A MCB to enable me to run an additional double socket via a radial circuit? Obviously the whole garage is protected by a 20A MCB in the house and RCD anyway. The wiring for the sockets in the garage is 2.5mm2.
Many thanks for any help!
  • Almost certainly yes.
  • Yes, but it may not be necessary. What are you intending to run from the sockets please?
  • Well actually you can safely add as many sockets as you like downstream of the 16a MCB using some more 2.5mm even without any further changes if you like. What you cannot do of course is draw much more than 16A total for any long period without the risk of the breaker doing its thing. However, the difference between a 20A and a 16A breaker is not that great (25% more load)  while in fact going the other way,  a 16A breaker and a 13A fuse are pretty similar too.
    IF you really want a lot more power in the garage, then you will need a larger supply - but if you are just plugging in a load of small stuff, or a few larger loads that are never all on at once, then it will be fine. Can you tell us the wattages or currents of the loads you are adding, and ideally the worst case combination ?
    M
  • Many thanks for your great reply!
    Absolute worst case is likely a fridge, dryer and one power tool such as a wood turning lathe/small miter saw/pressure washer. Unfortunately I don't have the wattages to hand as I've just moved in and they're all boxed up at the moment! I just thought 20A would give me a little headroom over the dryer & fridge for minor things and I'd most likely avoid having the dryer on whilst using power tools - I'm used to this from working in the old garage.
  • In your shoes, I'd add the sockets on the 16A branch for now, you will soon know if tripping is an issue, and then, only if it is,  then you can consider if it is safe to up-size either or both of the breakers.
    A twin and earth 2.5mm cable well cooled - i.e, in fresh air,  is good for 27A, however if it is enclosed in certain types of insulation, that useful rating can drop to less than 20A, so you cannot up-rate things by too much without checking the cable routes first.
    Come back for more advice about that aspect if you need it.
  • Perfect, thank you so much Mike!
  • The tumble dryer is arguably the greatest concern, since it probably uses about 10 amps and is a long hour load. Power tools are less of a problem as use tends to be intermittent  and short term
  • That depends very much upon the model. Heat pump driers are rated at about 5 A.