Why 70V rms and not 50V rms - O-PEN faults

Hi, always follow this forum as such a great source, so my first time with a question, hoping someone can advise.

Why `voltage between the cpc and earth exceeding 70V rms` for Reg. 722411.4.1 (iii) and not 50V as in Reg. 411 touch voltage threshold. Is 70V deemed acceptable ?

Parents
  • Hand to foot rather than hand to hand measurement.

    I agree that's the usual justification - but quite how reliable that is if there's metalwork stuck in the ground (sign posts, bollards) within reach of the vehicle, I'm less sure.

       - Andy.

Reply
  • Hand to foot rather than hand to hand measurement.

    I agree that's the usual justification - but quite how reliable that is if there's metalwork stuck in the ground (sign posts, bollards) within reach of the vehicle, I'm less sure.

       - Andy.