Why 70V rms and not 50V rms - O-PEN faults

Hi, always follow this forum as such a great source, so my first time with a question, hoping someone can advise.

Why `voltage between the cpc and earth exceeding 70V rms` for Reg. 722411.4.1 (iii) and not 50V as in Reg. 411 touch voltage threshold. Is 70V deemed acceptable ?

Parents
  • But one difference is that while an earth fault on a TN distribution circuit might be higher than 70V it's not going to persist for more than 5s - whereas 69.9999V could persist indefinitely as far as the open-PEN device is concerned.

       - Andy.

Reply
  • But one difference is that while an earth fault on a TN distribution circuit might be higher than 70V it's not going to persist for more than 5s - whereas 69.9999V could persist indefinitely as far as the open-PEN device is concerned.

       - Andy.

Children
  • whereas 69.9999V could persist indefinitely as far as the open-PEN device is concerned

    It could ... perhaps even higher if you think about measurement tolerances in the lab etc ... and in a real PEN fault, you might get touch-voltages in excess of CmaxU0 for up to 5 s which could also be problematic.

    But to fully understand what's going on here, we need to move away from the curves from IEC 60479-1 and use the values presented in IEC/TS 60479-5, which presents touch-voltage and duration values for different circumstances.

    NOTE: IEC 60479 series is not really intended to be a de-facto standard in its own right ... it's a 'horizontal standard' for consideration by committees developing electrical safety standards. Hence, what you see in those 'horizontal standards' won't always be reflected in a product or installation standard.

  • But one difference is that while an earth fault on a TN distribution circuit might be higher than 70V it's not going to persist for more than 5s - whereas 69.9999V could persist indefinitely as far as the open-PEN device is concerned.

    Which is why an additional control measure would have merit. The Zappi by MyEnergi,  for example, has an on board device that disconnects the supply to the EV, including the cpc when a current of circa 12mA is detected in the cpc. Obviously, someone has to touch the vehicle before the device operates but that is no different to additional protection by RCD to mitigate against direct contact.