Why 70V rms and not 50V rms - O-PEN faults

Hi, always follow this forum as such a great source, so my first time with a question, hoping someone can advise.

Why `voltage between the cpc and earth exceeding 70V rms` for Reg. 722411.4.1 (iii) and not 50V as in Reg. 411 touch voltage threshold. Is 70V deemed acceptable ?

Parents
  • including internal earth leakage able to detect a low as 6mA DC

    That function isn't directly to prevent electric shocks - but to prevent "ordinary" kinds of RCD being locked out by a d.c. residual current (a feature that used to be considered useful and was made use of by certain "D-loc" loop testers, to prevent RCDs tripping during high current loop tests but these days is rather a drawback - especially when you have a tub full of batteries, already with deliberate connections to the c.p.c.). A-type RCDs are tolerant of d.c. residual currents up to 6mA - hence if you have one of these 6mA RDC-DDs in the charge point, you can use an ordinary A-type RCD upstream ... if not you'll be looking at a B-type which can directly monitor d.c. residual currents - but sit down before asking for the price of one of those!  A 30mA B-type RCD will allow a d.c. residual current of up to 60mA before tripping.

       - Andy.

Reply
  • including internal earth leakage able to detect a low as 6mA DC

    That function isn't directly to prevent electric shocks - but to prevent "ordinary" kinds of RCD being locked out by a d.c. residual current (a feature that used to be considered useful and was made use of by certain "D-loc" loop testers, to prevent RCDs tripping during high current loop tests but these days is rather a drawback - especially when you have a tub full of batteries, already with deliberate connections to the c.p.c.). A-type RCDs are tolerant of d.c. residual currents up to 6mA - hence if you have one of these 6mA RDC-DDs in the charge point, you can use an ordinary A-type RCD upstream ... if not you'll be looking at a B-type which can directly monitor d.c. residual currents - but sit down before asking for the price of one of those!  A 30mA B-type RCD will allow a d.c. residual current of up to 60mA before tripping.

       - Andy.