Why 70V rms and not 50V rms - O-PEN faults

Hi, always follow this forum as such a great source, so my first time with a question, hoping someone can advise.

Why `voltage between the cpc and earth exceeding 70V rms` for Reg. 722411.4.1 (iii) and not 50V as in Reg. 411 touch voltage threshold. Is 70V deemed acceptable ?

Parents
  • https://pes-spdc.org/sites/default/files/shocking-electricity.pdf  has some fun extracts from the standards.

    Of course AC and wet feet will be rather different.

    The IEC figures tend to skate over this - once upon a time when it was the  IEE , UK regs  recommended 25V in place of 50V touch voltages for places that were likely to be wet, but this changing of limits based on the environment has not been the case for some years.

    You may find it amusing to note than the 1940s paper "Electric Shock as it Pertains to the Electric Fence," is still occasionally referenced, and that shows approximately a 4- 5 fold reduction in body resistance at low voltages when hands or feet are wet.

    The paper itself is still under copyright, but this public domain review of it https://incompliancemag.com/article/body-resistance-a-review/

    shows some key conclusions and re-creates the more interesting graphs.

    Mike.

  • UK regs  recommended 25V in place of 50V touch voltages for places that were likely to be wet, but this changing of limits based on the environment has not been the case for some years.

    Well, that's not quite the case either - SELV voltage limits (including those under fault conditions in the source) are still lower in 'wet' areas, such as Sections 701 and 702.

    BS 7671 has only really limited the magnitude of 'touch voltage' by supplementary local equipotential bonding - or, as above, in the permitted maximum voltage for SELV and PELV in some locations.

  • Well, true, but this thread is about car chargers and mitigation of network PEN lift,  and a car may be charged in the rain, and may  well be subjected to a greater rate of water flow than it would if it was installed under the shower in a lot of cheaper hotels, yet an EV charger  is scarcely operating at extra low voltage in any form !
    Equally, it is under those very conditions that one, if not wearing the ideal footwear, may well have wet socks electrically connecting to the puddle underfoot, and also perhaps wet hands.

    Personally I'm not sure that the '70V is OK for uninterrupted exposure for cars, but 50V for everything else' assumption is especially solid in such corner cases.

    Note that a few unlucky folk have been killed by 28V DC in military vehicles, but as far as I know, only when already wounded so badly the skin resistance was reduced or removed from the loop. A  study by Peng and Shikui (in 1995) presented autopsy results of 7 cases of electrocution by AC or DC voltages ranging from 25-85 Volts. Common factors wer the contact site was on or near the chest, the contact time was '“'long” , and skin burns and damage to internal organs were observed. Victims were otherwise healthy 20-41 year old males.

    In addition the authors note that the victims were working in high humidity and high temperature environments that

    1) increase susceptibility to electric shock through decreased skin resistance;

    2) decrease reaction time and ability to disengage from the voltage source;

    3) increase the chance of heatstroke/ unconsciousness as a result of exertion/fatigue.

    In terms of the 25V figure and UK regs,  I'm going back a long way - postwar I think, but long before regs were numbered in the current way, I'm pretty sure it was aimed at reducing accidents in shipyards etc.  I'll try and find out how far back tonight when I have more time to look at my archives of such ;-)
    Mike.

    EDIT

    Later than I thought - 1966 14th edition,

  • Later than I thought - 1966 14th edition,

    25V lasted a lot longer than that - blue cover 16th Ed (2001) section 605 (Agricultural) modifies the usual RA Ia ≤ 50V to 25V and likewise for supplementary bonding has R  ≤ 25/Ia

    Ditto for constructon sites (604).

    - Andy.

Reply
  • Later than I thought - 1966 14th edition,

    25V lasted a lot longer than that - blue cover 16th Ed (2001) section 605 (Agricultural) modifies the usual RA Ia ≤ 50V to 25V and likewise for supplementary bonding has R  ≤ 25/Ia

    Ditto for constructon sites (604).

    - Andy.