New Consumer Unit Necessary?

We are having our conservatory replaced with a more substantial "garden room". The electricity in the conservatory was a spur off a current ring main, and the new room will be the same. The electrician says we must have the current consumer unit (which is plastic and has no RCDs being ~30 years old) replaced in order for the work to be certified. We had the system checked a few years ago and although advised a new consumer unit would be better, told it was not a legal requirement.

So do regulation require a new consumer unit with RCDs for this ring spur to be re-added, or is he being over cautious?

Parents
  • you would need an RCD spur for both legs of the ring

    I don't see that working - any tiny difference in L / N resistance around the ring would mean that the L & N currents in each leg wouldn't precisely balance - so quite likely both RCDs would trip even without any leakage to earth.

      - Andy.

Reply
  • you would need an RCD spur for both legs of the ring

    I don't see that working - any tiny difference in L / N resistance around the ring would mean that the L & N currents in each leg wouldn't precisely balance - so quite likely both RCDs would trip even without any leakage to earth.

      - Andy.