1.2kohm from stop tap to met although fed by copper pipe and then plastic pipe.

As above a 1 meter section of plastic pipe joins onto the lead watermain under the floor,whilst the gas supply

pipe passes through a brick wall and awaits the gas meter to be fitted.My thoughts are that the gas pipe through

the wall is giving the low reading,but could the water in the plastic also be contributing since it connects to the lead?

Gas and water pipes are glanded into the boiler,which is not electrically connected atm.I have main bonded gas

and water,although in theory the water does not need bonding.Thanks for any advice.

                                                                                                    Regards,

                                                                                                           Hz

Parents
  • I assume this figure is pre the addition of any bonding in this house, but what about the neighbours - they may well have bonding from MET to water pipes. even if external gas is plastic. Actually 1k2 sounds very high for that, I;d hjave expected single figures to sub ohm.

    Water in 15mm or 22mm plastic pipes, unless undrinkably contaminated (and with the various treatments, pipes in heating systems can be) will be tens to hundreds of k ohms per metre of length, so there is at least one parallel path.

    M

Reply
  • I assume this figure is pre the addition of any bonding in this house, but what about the neighbours - they may well have bonding from MET to water pipes. even if external gas is plastic. Actually 1k2 sounds very high for that, I;d hjave expected single figures to sub ohm.

    Water in 15mm or 22mm plastic pipes, unless undrinkably contaminated (and with the various treatments, pipes in heating systems can be) will be tens to hundreds of k ohms per metre of length, so there is at least one parallel path.

    M