EICR TT installation coded C2 by electrician

Hi,


Anybody got any thoughts on this situation?

I have had an EICR done on a property. There were no issues reported apart from earthing. 

The electrician measured the rod resistance at 534 ohms. He insists it has to be less than 200, but his preference is less than a 100.
He said the 30ma RCD wouldn't trip at the measured value, so didn't bother to test it. Bizarrely, he said he pressed the test button which, of course, tripped, but he coded it C2 "unsatisfactory".

I had already tested it with my meter. I got 400ohms, a worst case trip time of 9ms, best 6ms and 28ma on the ramp test.

I pointed out the 200ohms is a recommendation not a requirement and asked him to justify his C2, he refused and stated he stands by his findings.

I haven't checked yet if there is an obvious reason for the rod to be high, but it seems to me the requirements of the regulations have been met.


Parents
  • There are situations where a reading that high can mean the electrode has all but corroded away, but at 500 ohms it would trip the RCD and is not an immediate fail.

    As described, I would suggest 'needs improvement' C3 or at least 'needs investigation' but there may be other things we cannot see that concerned him.

    If the soil is very dry and sandy or shingle, it is entirely reasonable to get a reading of some hundreds of ohms from a single electrode, and in that case a rod may be the wrong thing, but  arguably in such places it is also hard to get a shock to true earth as well and of little concern.

    Mike.

Reply
  • There are situations where a reading that high can mean the electrode has all but corroded away, but at 500 ohms it would trip the RCD and is not an immediate fail.

    As described, I would suggest 'needs improvement' C3 or at least 'needs investigation' but there may be other things we cannot see that concerned him.

    If the soil is very dry and sandy or shingle, it is entirely reasonable to get a reading of some hundreds of ohms from a single electrode, and in that case a rod may be the wrong thing, but  arguably in such places it is also hard to get a shock to true earth as well and of little concern.

    Mike.