EICR TT installation coded C2 by electrician

Hi,


Anybody got any thoughts on this situation?

I have had an EICR done on a property. There were no issues reported apart from earthing. 

The electrician measured the rod resistance at 534 ohms. He insists it has to be less than 200, but his preference is less than a 100.
He said the 30ma RCD wouldn't trip at the measured value, so didn't bother to test it. Bizarrely, he said he pressed the test button which, of course, tripped, but he coded it C2 "unsatisfactory".

I had already tested it with my meter. I got 400ohms, a worst case trip time of 9ms, best 6ms and 28ma on the ramp test.

I pointed out the 200ohms is a recommendation not a requirement and asked him to justify his C2, he refused and stated he stands by his findings.

I haven't checked yet if there is an obvious reason for the rod to be high, but it seems to me the requirements of the regulations have been met.


Parents
  • FI is probably a better code, still a fail but certainly worth investigating.  If it gets a C3 nothing will get done about it and it could fail if there is an issue other than just a rocky or sandy area.

    Gary

  • FI should only be used (see best practice guide) if a determination can not be made. The installation is compliant with the the max resistance and the disconnect times are more than adequate. The requirement is "is it safe" not "is it perfect". 

  • Err, and is it reasonable on the evidence presented to expect it will it stay safe and regs compliant until the recommended date of the next inspection, assuming no unnatural abuse  ? You may prefer a very short retest interval ?

    Now if that high Z is due to sandy or stony ground and the electrodes and connections to them are in good order fair enough. If however it is in soil that normally gives 50 ohms for a 4 ft rod, then something is wrong, and it may in fact be almost corroded away and hanging by a thread and ready to fail at any moment. The meter alone cannot tell - the mk1 eyeball and perhaps a bit of a waggle of the electrode(s?) and associated clamp(s) is the level of 'FI' needed here.

    M.

Reply
  • Err, and is it reasonable on the evidence presented to expect it will it stay safe and regs compliant until the recommended date of the next inspection, assuming no unnatural abuse  ? You may prefer a very short retest interval ?

    Now if that high Z is due to sandy or stony ground and the electrodes and connections to them are in good order fair enough. If however it is in soil that normally gives 50 ohms for a 4 ft rod, then something is wrong, and it may in fact be almost corroded away and hanging by a thread and ready to fail at any moment. The meter alone cannot tell - the mk1 eyeball and perhaps a bit of a waggle of the electrode(s?) and associated clamp(s) is the level of 'FI' needed here.

    M.