"it is that pesky SY braided stuff again; so what's wrong with it"

More a discussion come question perhaps, but are there any really good reasons why a choice of SY would be made for a fixed wire low voltage power circuit  over something else ?

My understanding of the braiding,  is that it has nothing to do with armouring and is not acceptable as armouring;  but is it still an exposed conductive part to be earthed and if it is not [earthed], how much of a risk  ?

from reading Eland (who have a pdf on the SY stuff) to mention one manufacturer, is that it is a somewhat standards tested cable (https://www.elandcables.com/media/13rlt2rk/ec-statement-on-the-use-of-sy-cy-yy-cables-rina-18th-ed-with-summary.pdf)

In the case observed being a 3phs circuit, it was 5core (one as cpc) from a metal db (through plastic stuffing gland) to a plastic interlock socket, 16a 3pole mcb and it appeared the braiding was unterminated.   it was not on a run likely to be disturbed.   Nothing noted on the EIC about its use either.

regards

Habs

Parents
  • I think Andy's answers are the generally-accepted wisdom.

    I suppose there is some difference in that generally we'd expect a c.p.c. to remain serviceable after a fault (so for example it can't be allowed to get so hot it permanently damages surrounding insulation) whereas an exposed-conductive-part might be considered more expendable

    A good reason to use the correct glands at BOTH ends of the cable, so there are parallel cpc paths in the event of penetration or severing of the outer layers of the cable.

Reply
  • I think Andy's answers are the generally-accepted wisdom.

    I suppose there is some difference in that generally we'd expect a c.p.c. to remain serviceable after a fault (so for example it can't be allowed to get so hot it permanently damages surrounding insulation) whereas an exposed-conductive-part might be considered more expendable

    A good reason to use the correct glands at BOTH ends of the cable, so there are parallel cpc paths in the event of penetration or severing of the outer layers of the cable.