SELV Supplies to Motorised Smoke Dampers

On a job I am working on, a 2 core and bare earth FP200 plus has been run to pick up Motorised Smoke Dampers.

The dampers that arrived onsite are fitted with BEN24 actuators and on looking them up it seems they are a 3-wire system, one wire to rotate to the open position and one to rotate to the closed position with a common return.

If the supply to these actuators is at 24V DC, am I correct to assume that I can use the full size bare CPC of the FP200 plus as the common return and the two cores for each of the "positive" poles or is my understanding of regulation 414.4.5 incorrect?

Parents
  • I agree with Graham - I'd note that basic protection isn't quite the same thing as basic insulation  - basic protection being more to do with prevention of electric shock without a fault being present (direct contact in old money), while basic insulation (functional insulation in old money) often does provide basic protection, it can also be needed for other purposes - functional insulation of course, but also helping to prevent shock under fault conditions (including faults on other circuits).

       - Andy.

Reply
  • I agree with Graham - I'd note that basic protection isn't quite the same thing as basic insulation  - basic protection being more to do with prevention of electric shock without a fault being present (direct contact in old money), while basic insulation (functional insulation in old money) often does provide basic protection, it can also be needed for other purposes - functional insulation of course, but also helping to prevent shock under fault conditions (including faults on other circuits).

       - Andy.

Children
  • Yes, correct on all the statements you mentioned.

    The reason i am inclined to say i am correct with my assumption is that the two positive cores will be insulated therefore providing the functional insulation role even though the negative pole is uninsulated and the voltage will be below 30V DC as per the reg. Similar to trucks where the negative pole is effectively the chassis (BS 7671 does not apply to the automotive industry). All connections including the bare conductor will be enclosed in a plastic junction box and not in publicly accessible locations.

    Section 715.414 makes reference to bare conductors for SELV lighting when the voltage level is below the regs limits.