Shaver socket installation

Dear IET forum,

I'd like to get a shaver socket installed in a cupboard that used to hold an immersion heater, adjacent to the bathroom. The cupboard currently has a standard single socket, supplied direct from the consumer unit by a dedicated supply with an MCB rated at 16 amps that I presume used to power the heater. This circuit doesn't supply power to anything else, nor do I plan for it to do so.

Ideally, I'd like to use the existing wiring, rather than running the shaver socket off either a ring main or lighting circuit. Questions:-

1) is this possible?

2) would it only require someone to replace the MCB with one at a lower rating of, say, 3A and install the shaver socket?

3) would it be necessary to install a 3A FCU to protect the shaver socket? If so, would a change to the MCB also be necessary?

Many thanks

Leo

Parents
  • Personally, I would just buy a plug-in shaver adaptor from a hardware store and call it "job done".

    But...

    1. Yes.

    2. Why? The MCB should be specified to protect the cable, not what's connected to it.

    3. Only if the manufacturer's instructions call for a fused supply.

Reply
  • Personally, I would just buy a plug-in shaver adaptor from a hardware store and call it "job done".

    But...

    1. Yes.

    2. Why? The MCB should be specified to protect the cable, not what's connected to it.

    3. Only if the manufacturer's instructions call for a fused supply.