Earth Potential Rise risk with TT earth close to Pole Transformer.

I'm looking at the risks associated with Earth Potential Rise Risk in TT an installation close to a Pole Transformer. I have read from the various DNO's they specify a distance between the HV earth and the LV earth, this I'm taking is to avoid the EPR from the HV side being transferred to the earth of the LV side.

This is based on sites being close to or within the distances mentioned above.

I have seen sites that have a DNO TN-C-S earth provided, but there seems a risk. In the event of the HV fault, even if the separation between the LV and the HV earths to reduce the EPR transfer to a safe potential. In the TN-C-S earth there will be a voltage on the earth from the HV fault, this voltage will be present at the DNO head cut out. Which will effectively cause a potential between the DNO earth and local earth.

I would consider a TT earth to mitigate the above. While the earth will bring in the Local earth voltage if there is one from the EPR from a HV Fault, it will effectively create a equipotential zone at what evert the EPR is at that point.

Any advise or references would be greatly appreciated.

Parents
  • While the DNO likely don't know where their electrode is, they should be able to tell you whether it's a hot or cold substation, because if it's hot it should be on the hot site register. Hot/cold relates to the EPR, which doesn't give you all the answers but does give you a hint as to scale of the issue, if there is one (and there may also be explicit exclusions along the lines of "Don't install anything earthed within this area")

    Each DNO will have its own policy, for internal use, on combined and separate earthing systems; for example WPD/NGED TP21D/3. Of course that only applies to their network wheras a new TT rod will not be within scope. Any bare connection to earth within the zone may well be verboten under the terms of the connection agreement (not least to protect everyone else on the supply from transferred potential).

    Note that if you are importing an LV supply from further away back into the hot zone, you might actually also be in need of an isolation transformer, since not only will E be referenced to some other bit of soil, but by definiton also the transformer star point and hence L123N, so you could suddenly see L or N swing high with respect to your local earth. This happens, for example, on DNO substations with an auxiliary supply fed from the LV network, but also on some commercial sites too.

Reply
  • While the DNO likely don't know where their electrode is, they should be able to tell you whether it's a hot or cold substation, because if it's hot it should be on the hot site register. Hot/cold relates to the EPR, which doesn't give you all the answers but does give you a hint as to scale of the issue, if there is one (and there may also be explicit exclusions along the lines of "Don't install anything earthed within this area")

    Each DNO will have its own policy, for internal use, on combined and separate earthing systems; for example WPD/NGED TP21D/3. Of course that only applies to their network wheras a new TT rod will not be within scope. Any bare connection to earth within the zone may well be verboten under the terms of the connection agreement (not least to protect everyone else on the supply from transferred potential).

    Note that if you are importing an LV supply from further away back into the hot zone, you might actually also be in need of an isolation transformer, since not only will E be referenced to some other bit of soil, but by definiton also the transformer star point and hence L123N, so you could suddenly see L or N swing high with respect to your local earth. This happens, for example, on DNO substations with an auxiliary supply fed from the LV network, but also on some commercial sites too.