DNO requirement for protective bonding
It is very common in NI for NIE to refuse connection to a domestic installation unless main protective bonding is in place to the water service pipe, even when it is the blue plastic type. Sparkies have to fit a copper insert in the plastic pipe to install the bonding clamp.
I cannot imagine why they insist on this, but insist they do! I was wondering if anyone has similar experience in other regions.
Parents
  • In which case Andy, it begs the question as to why hundreds of metres of 10mm singles are thrown into installations across the land with each rewire carried out. Why bother when you can just utilise the 1.0mm/1.5mm cpc from an appliance metallic pipework to the incoming gas & water supplies!
    it certainly make a difference when when pipework is truly extraneous - (either at the incoming position, or dives out underground somewhere to say an outside tap or  another building) - you really don't want large fault currents from elsewhere or diverted neutral currents on PME systems being forced down a 0.75mm² c.p.c..  But in many cases these days (with plastic plumbing) that simply can't happen - and to be fair BS 7671 definitions have supported that stance for very many years (if something doesn't meet the definition of an extraneous-conductive-part you don't have to bond it).
Reply
Children
No Data