Just taking Item/row 1 as an example in Table 4C1 - The way I read it is that for up to 9 cables/circuit, you read the rating factor directly and for 9-11 cables/circuits use 0.5, for 12-15 use 0.45, for 16-19 use 0.41 and for 20+ use 0.38…?
well yes, but I'd caution that really by the time you get to bundles that big it is not a great assumption that a single figure applies. Obviously the escape route for heat generated by the cable in the bundle centre is the limiting factor, and if the bundle is non uniform - perhaps slightly elliptical rather than circular then the distance from centre to edge is is not the same. You could squeeze a bit more by putting more lightly loaded circuits in the middle.
In the end the tables are guidance - at some point a measurement is more helpful, and often complex cable routes are such a case.
Mike
well it is not really made clear I agree - I suppose you could plot a curve of the points given to get a more precise, but no more accurate figure for a bundle size not given, but the adjacent value is usually a good starting point. Personally, I prefer to wrap max indicating temperature stickers into things I expect to run close to the limit, and round bunches of cable are a bad idea anyway - a 'ribbon' layout on basket is much nicer.if you possibly can or loose to allow free air flow.
Mike.
well it is not really made clear I agree - I suppose you could plot a curve of the points given to get a more precise, but no more accurate figure for a bundle size not given, but the adjacent value is usually a good starting point. Personally, I prefer to wrap max indicating temperature stickers into things I expect to run close to the limit, and round bunches of cable are a bad idea anyway - a 'ribbon' layout on basket is much nicer.if you possibly can or loose to allow free air flow.
Mike.