Isolation Transformer and its Secondary Protection

When using an isolation transformer in a control panel. in this case for  a motor heater, I think I should probably tie 0V to earth within the control panel.

- I would also like to protect the secondary, however what are the rules here, do you have to provide 2P MCB?

-Obviously I have an upstream 2P MCB of the transformer.

- I would think its perfectly OK to use only a single pole on MCB on the line side output of the transformer?

Does anybody have any comments on this?

Parents
  • Hi

    Thanks folks, really helpful..........Some more info:

    - The Primary voltage is 230Vac and secondary for the motor heater is 110Vac.

    - Happy to disconnect on first fault, its non-critical.

    - Not sure what this means "functional requirements about earthing ].

    - And ADS would be shock protection for the heater.

    - Wattage would be between 50 and 100W for a small heater.

    Thanks