Wonder what your thoughts are on this.
Installing an extra cooker connection point on an existing circuit. the circuit is protected by a 80A type AC rcd and 32A MCB.
It's going to be powering an oven plus an induction hob to be added, so should be on a type A RCD.
Problem is that Schneider only have a 63A type A rcd for over £100 before vat.
But interestingly the type AC device tripped in 19mS with a *1 type A rcd test.
So I am thinking maybe I don't need to worry about changing the RCD, what are your thoughts.
If I do change I will probably have to go for an RCBO