Wiring Regs scope, inside 19" rack cabinets?

Hi everyone,

The US-based company I work for needs to send a 19" rack cabinet of computers, PLCs and network equipment to the UK for temporary installation in a research facility. We've been advised (quite rightly) that we need to ensure compliance with UKCA marking requirements and be able to provide a technical file for this. It's been a while since I was involved in compliance things, but my understanding is that the technical file is normally just about demonstrating compliance with the harmonised norms, e.g the low voltage directive. However as this will be a cabinet "installed", i.e. fixed, in position, with power distributed within it, I wondered if it is also in scope of the BS 7671?

Advice much appreciated on this, especially from anyone with practical experience of a similar situation.

Thanks,

Will

Parents
  • I've installed a fair bit of US originated kit in the UK over the years (IT kit in racks normally), all according to the supplier's instructions.  The black/white/green core colours in the flex can be dealt with by over-sleeving at the terminations on the "UK" end. Voltages are usually OK but worth checking - we typically won't have 115V available, and 230V will have a earthed N - whereas US 230V is typically from a 115-0-115 system - so PDUs come with DP MCBS - which is fine if overkill for the UK. Just check that there aren't any 115V items lurking in there anywhere (small things cooling fans for the top of the rack come to mind).

       - Andy.

Reply
  • I've installed a fair bit of US originated kit in the UK over the years (IT kit in racks normally), all according to the supplier's instructions.  The black/white/green core colours in the flex can be dealt with by over-sleeving at the terminations on the "UK" end. Voltages are usually OK but worth checking - we typically won't have 115V available, and 230V will have a earthed N - whereas US 230V is typically from a 115-0-115 system - so PDUs come with DP MCBS - which is fine if overkill for the UK. Just check that there aren't any 115V items lurking in there anywhere (small things cooling fans for the top of the rack come to mind).

       - Andy.

Children
  • Hello, thank you for the helpful suggestions. the cabinet is already wired so if we're not using the right colours oversleeving is probably the quickest solution, unless we find that the cable itself is not properly rated. We've already got a PDU in there: https://www.startech.com/en-us/server-management/pdu08c13h.

    I feel at this point there's a risk that I start listing all the components and eventually providing a wiring diagram which probably isn't appropriate so I won't keep going. You've all been very helpful and I don't want to take advantage of that.

  • Ah well, if the PDU has a C20/C19 inlet - then the simplest thing might be just to plug a UK lead into that - e.g. https://uk.rs-online.com/web/p/power-cords/3119315 (or more likely with a blue 16A BS EN 60309 plug).

       - Andy.

  • Yes, since we _can_ use plugs we should. We'll confirm how the local electrical supply will be provided. Cheers Slight smile

  • When you do the confirming in your shoes I'd be forcing it a bit. Along the lines of (but delete what you do not want)

    "

    The rack will consume up to Xxx  watts at 230VAC single phase.

    So we can provide a suitable lead, can you confirm that  the supply will be one of the following, and which is your preferred.

    13A socket to BS1363

    (do not offer this if there is any doubt it may not be enough, say more than 2000 watts or if you do not want it to share a breaker and RCD (GFI) with everything else of no great importance in the building)

    16A blue single phase socket to BS EN 60309

    32A single phase socket BS EN 60309

    Flex to bare ends for your non standard termination (not preferred)

    Unless otherwise requested the supplied lead will be nominally ~1.8m (6 feet) long from the bottom left rear of the rack.

    Or where ever it exits from the rack, so they know where to put the socket.

    "

    Avoids doubt, and allows them to get power to the right place at their end in advance. Anything more than the 13A socket will probably have them running in a new line, in 2,5mm cable or larger for the 16A or 4mm cable or larger for the 32A, and that is likely to be more reliable, as no-one will then unplug it  to use the vacuum cleaner....

    Mike

  • Good shout Mike, thank you, we'll get a suitable cable with a plug which meets the hosts needs.