What does a EV charging point actually do?

I have bought a 2nd hand Nissan leaf and have been happily charging it slowly from a 13A socket (fed by solar panels) for 6 months using the "granny lead" that comes with the car.

Yesterday, when I turned it on, the READY and CHARGE light flashed about once per second, as did the lights on the dashboard, and there was a click each time from the unit. The manual does not list this combination as indicative of anything.

This lead me to wonder what the "charging unit" actually does, It lists its input and output as 250V ac so it clearly is not a transformer/ rectifier. If it is a protective relay measuring neutral earth voltage, then maybe the ON / OFF is caused by something happening to the voltage in the house?

I have not found any information on the internet as to what is inside these units.

Parents
  • I have not found any information on the internet as to what is inside these units.

    It occurs to me that the one certain way of finding out would be to take the lid off and have a look.

  • seconded, And when you do, let us know, feel free to post pics of any part you cannot identify  ;-) I know what is inside all sorts of kit, including as it happens a couple of makes of the larger chargers  by exactly this method, not by some course.

    M,

  • have not found any information on the internet as to what is inside these units.

    It occurs to me that the one certain way of finding out would be to take the lid off and have a look.

    Not sure what you're looking for exactly as to the extent of what's in there, but this site has a good brief description: https://www.rfwireless-world.com/Terminology/EV-charging-modes.html

    In short, the safety features built into the lead are:

    • Built-in RCD
    • Circuit to monitor the resistance between PE and N to demonstrate the earthing is likely to be safe (at least will operate RCD)
    • Circuit to communicate with the vehicle, so power is not applied to the vehicle connector end of the cable until the vehicle is connected. Also, removes power if the vehicle comms fails.

    Ignoring the RCD, the electronics required for the above functions are not extensive. There are various circuits available on the internet, based on those in the standards for the devices.

Reply
  • have not found any information on the internet as to what is inside these units.

    It occurs to me that the one certain way of finding out would be to take the lid off and have a look.

    Not sure what you're looking for exactly as to the extent of what's in there, but this site has a good brief description: https://www.rfwireless-world.com/Terminology/EV-charging-modes.html

    In short, the safety features built into the lead are:

    • Built-in RCD
    • Circuit to monitor the resistance between PE and N to demonstrate the earthing is likely to be safe (at least will operate RCD)
    • Circuit to communicate with the vehicle, so power is not applied to the vehicle connector end of the cable until the vehicle is connected. Also, removes power if the vehicle comms fails.

    Ignoring the RCD, the electronics required for the above functions are not extensive. There are various circuits available on the internet, based on those in the standards for the devices.

Children
  • Thank you for this.

    The original question relates to my charger cycling on and off at about once per second. I am trying to resolve whether this is likely to be normal, a fault in the car, a fault in the charger or a fault with my home wiring.

    The local Nissan agent has offered to run a diagnostic on the car for £100, but this may well find nothing as the fault only seems to be present within half an hour of using the car.

    From all the helpful answers, I am coming to the conclusion that the charger is switching on and off because the car is requesting it to, i.e. a fault in the car, maybe it is sensing a hot battery and switching off only to say that it is OK and switch on again.

    I had the idea that it might relate to a high neutral earth voltage in the house, which would only show up when the charger was on, but measuring this showed the NE voltage steady at well below 1V at the time.

  • I had the idea that it might relate to a high neutral earth voltage in the house, which would only show up when the charger was on, but measuring this showed the NE voltage steady at well below 1V at the time.

    The car itself may also be looking for a minimum neutral-earth resistance.

    Have you checked loop impedance and connections at the socket-outlet to see if anything has changed?

    What is the earthing arrangement, and is the solar array/inverter grid-connected when you are charging the car? I'm also assuming you've tried it in another installation?