Hello

i have a customer who currently has a 250Amp section board with no neutral conductor. (a 3 core cable installed for 3 phase and a separate earth) some new equipment is being installed that requires a neutral. I've been asked to get a neutral into the box. 

is there any reason why i cant just add a separate neutral conductor. id argue its not best practice, but is it against regulation. ive had a good look and cant see anything that says no.

your thoughts and input are appreciated

Parents
  • ive had a good look and cant see anything that says no.

    :

    indeed a 3 core SWA

    Regs wise 521.5 - the steel armour counts as a ferromagnetic enclosure - there's an exception for additional c.p.c.s (3rd para of 521.5.1) but not for neutrals.

      - Andy.

Reply
  • ive had a good look and cant see anything that says no.

    :

    indeed a 3 core SWA

    Regs wise 521.5 - the steel armour counts as a ferromagnetic enclosure - there's an exception for additional c.p.c.s (3rd para of 521.5.1) but not for neutrals.

      - Andy.