installing a separate neutral conductor

Hello

i have a customer who currently has a 250Amp section board with no neutral conductor. (a 3 core cable installed for 3 phase and a separate earth) some new equipment is being installed that requires a neutral. I've been asked to get a neutral into the box. 

is there any reason why i cant just add a separate neutral conductor. id argue its not best practice, but is it against regulation. ive had a good look and cant see anything that says no.

your thoughts and input are appreciated

Parents
  • Dont disagree with the answers already given, but given you have to install 120M of "Neutral" conductor between A and B plus treminate correctly that single conductor and be happy design and install is compliant with BS7671. Surely the labour and install costs of a 4mm or 6mm SWA for that new load will be similar if not less expensive, you design a dedicated final circuit and issue a EIC then both you and client know there is full compliance with regs and leave existing as is??

    GTB

Reply
  • Dont disagree with the answers already given, but given you have to install 120M of "Neutral" conductor between A and B plus treminate correctly that single conductor and be happy design and install is compliant with BS7671. Surely the labour and install costs of a 4mm or 6mm SWA for that new load will be similar if not less expensive, you design a dedicated final circuit and issue a EIC then both you and client know there is full compliance with regs and leave existing as is??

    GTB