Diverted neutral current / broken PEN?

Hello all,

Diverted Neutral Currents (DNC) seem to be a big area for debate especially with the push for EV's and the implications that they can cause.

Are there any official figures regarding contacting the DNO regarding these DNC's or recording of it other than on testing documentation (EIC/EICR etc.) ?

This still seems to be an area that needs more information, as variations including the location of the fault, the time of day, year etc. when the test was completed.

If testing a standard PME 100A single phase domestic supply and getting around 8mA on the earthing conductor during the installation being switched on and then reduces 0.01mA when the installation is isolated will probably be more to do with the instrument and 0.01mA = 0.00001A and would indicate that there is no issue. If this stayed at 8mA (0.008A) this is potentially an issue with a broken/deteriorating PEN conductor, however this could change due to variations across neighbouring installations.

When completing this test prior to any other work on the installation and getting readings when not expecting them this is going to impact on any electrical work being carried out, what is deemed as notifiable to the DNO? 

I have heard of anything 5A and above being reportable to the DNO which seems reasonable, however what if you were to get a reading of 4.5A, due to those variations this could be higher taking it beyond the 5A at other points in the day etc.

Would it be more appropriate to have anything above 1A reportable to the DNO so they can make their checks and note this on the job/ testing documentation, and where does it become a safety issue regarding work in/on the installation with a broken/deteriorating PEN conductor, as a job could be completed and several weeks later an incident could occur due to further loading and changes to an installation?

There is lots of information, about how and why etc, but no physical figures, I am aware that Smart metering maybe able to measure volts/current/power etc however this still seems a little vague.

Parents
  • This is quite timely for me because I was pondering asking a question in a new thread.

    So this afternoon, in rough terms, 12 A in the line, 9.0 A in the neutral, and 3.0 A in the earthing conductor. 0.05 A in the gas bonding. (The plastic water pipe is also bonded!)

  • (The plastic water pipe is also bonded!)

    That will  be nanoamps then. Probably more current flowing through any layer of fingerprints, condensation or building detritus on the outside of the polypipe.

    The other two at least have the decency to add up OK, which suggests first that it is mostly your own current rather than the neighbours, so that is nice, and secondly that the two impedances are largely resistive, or at least if they are not then the ratio of L to R is very similar in both paths.

    3 out of 4 electrons prefer the official neutral path if you like to see the world that way.

    Mike

  • So this afternoon, in rough terms, 12 A in the line, 9.0 A in the neutral, and 3.0 A in the earthing conductor. 0.05 A in the gas bonding. (The plastic water pipe is also bonded!)

    Possible that's just "normal" operation if the gas is also bonded to other installations. But on the other hand ...

    ... So, was Ze OK with DNO earthing conductor disconnected from MET? ... Again, no exact science with PME, but a poor Ze with those conditions could indicate a PEN fault!

  • The open circuit voltage revealed  during any such a test may be of interest/ concern as well.

    Mike

  • Graham, thank you. I was thinking that perhaps I should test the Ze because I cannot quite figure out where the current is going, or even in which direction. If there were any significant current in the gas bonding, all would be explained, but that is not the case. Another possibility is that the current is going via various supplementary bonding conductors to the CH boilers and pipes and getting into the gas main that way.

    So I shall give myself an "FI" and let you know the reading when I get home later.

  • Another possibility is that the current is going via various supplementary bonding conductors to the CH boilers and pipes and getting into the gas main that way.

    Absolutely, other fortuitous earth paths are a possibility also. What we don't know is the direction of 3A in the earthing conductor and the 9 A in the neutral conductor, and/or (although I'm sure you've discounted for this particular installation) whether there's an N-E fault in the installation?

Reply
  • Another possibility is that the current is going via various supplementary bonding conductors to the CH boilers and pipes and getting into the gas main that way.

    Absolutely, other fortuitous earth paths are a possibility also. What we don't know is the direction of 3A in the earthing conductor and the 9 A in the neutral conductor, and/or (although I'm sure you've discounted for this particular installation) whether there's an N-E fault in the installation?