Hi, is there any specific date set as to when the Code of Practice for Electric Vehicle Charging Equipment Installation, 5th Edition will be available. 

Parents
  • Has anyone got a copy of the book or the electronic version?

    Does EVSE Code of Practicel still recommend the use of a Pen fault detector?  I do think the concept is good but

    without BSEN or a letter of conformity or product standard and without a defined way to test it, it seems rather counter intuitive.  It seems that a BS EN for Pen fault detectors needs to be expedited as in effect it is a dependancy of the PEN fault detector. 

    Once this is in place (BS EN) the PEN fault detector can be

    Designed, Selected and Errected

    Installed

    Comissioned

    Tested

    Signed off

Reply
  • Has anyone got a copy of the book or the electronic version?

    Does EVSE Code of Practicel still recommend the use of a Pen fault detector?  I do think the concept is good but

    without BSEN or a letter of conformity or product standard and without a defined way to test it, it seems rather counter intuitive.  It seems that a BS EN for Pen fault detectors needs to be expedited as in effect it is a dependancy of the PEN fault detector. 

    Once this is in place (BS EN) the PEN fault detector can be

    Designed, Selected and Errected

    Installed

    Comissioned

    Tested

    Signed off

Children
  • Has anyone got a copy of the book or the electronic version?

    Does EVSE Code of Practicel still recommend the use of a Pen fault detector?

    Yes, and yes.

    without BSEN or a letter of conformity

    Shouldn't all products subject to the Electrical Equipment (Safety) Regulations had a DofC regardless of whether there is a harmonized/designated standard?

    The standards route is not the only way for a manufacturer to comply with the legislation, and this is the case specifically to permit new technology, or "one-off" products or assemblies for a particular project.

    Notes to Regulation 722.411.4.1 tells you the minimum BS 7671 requires for the installation paperwork if the devices are used in an installation.