Two Distribution boards supplied by one sub-main

I'm in the middle of a 'discussion' over an EICR in which the contractor is claiming that two distribution boards (in different parts of the building) but fed from the same sub-main (well, split on the outgoing terminals of the supplying switch fuse) is a C2 and needs to be changed.

He is unwilling to supply a regulation which he feels this contravenes and I'm struggling to find such a reg.

What is the opinion of the learned community?

I think this is perhaps not best practice but I'm struggling with his assertion of a C2.

Comments please...... 

Parents
  • On the face of it i can't see why it would be coded at all. it's a poor design and could be inconvenient that's all.Might have been the only option when installed.  It obviously isn't overloading the fuse . There is no possible danger that i can see. At the very most C3.   Gary