Individual EVC's wired over 3-phases

Hello all

Please could anyone advise of any issues for installing single phase EVC's from a 3 phase supply.

Proposing there are 6 x 7kW chargers that are located adjacent to each other and wired from individual phases of a 3-phase supply in a local feeder pillar.

Each single phase charger circuit is protected separately in accordance with 722.533.101. The query is if there are any comments on the adjacencies of the vehicles given they are wired on separate phases?  

Thanks in advance

Parents
  • Given that most cars could also take 3 phases as well as single phase charging, there really should be no problems. The important thing is that the earthing to all cars that may be simultaneously touched is common, so there is no risk of there being an exposed voltage difference.

    ~Mike.

  • Hi Mike

    Thank you for the response. Yes each charging point is taken from a common three phase distribution board with common earth. 