Individual EVC's wired over 3-phases

Hello all

Please could anyone advise of any issues for installing single phase EVC's from a 3 phase supply.

Proposing there are 6 x 7kW chargers that are located adjacent to each other and wired from individual phases of a 3-phase supply in a local feeder pillar.

Each single phase charger circuit is protected separately in accordance with 722.533.101. The query is if there are any comments on the adjacencies of the vehicles given they are wired on separate phases?  

Thanks in advance

Parents
  • 514 refers. 

    The current regs only require labelling when there's a nominal voltage to earth in excess of 230V - there's no such voltage on a 3-phase 400/230V system.

    The requirement to label when there was >250V between conductors went the way of the dodo decades ago.

       - Andy.

Reply
  • 514 refers. 

    The current regs only require labelling when there's a nominal voltage to earth in excess of 230V - there's no such voltage on a 3-phase 400/230V system.

    The requirement to label when there was >250V between conductors went the way of the dodo decades ago.

       - Andy.