Individual EVC's wired over 3-phases

Hello all

Please could anyone advise of any issues for installing single phase EVC's from a 3 phase supply.

Proposing there are 6 x 7kW chargers that are located adjacent to each other and wired from individual phases of a 3-phase supply in a local feeder pillar.

Each single phase charger circuit is protected separately in accordance with 722.533.101. The query is if there are any comments on the adjacencies of the vehicles given they are wired on separate phases?  

Thanks in advance

Parents Reply Children
  • That sign , or an UK styled version of it, might be more or less OK for a split single phase supply 230-0-230 common on farms where the DNO bottled at the expense of bringing the 3rd HV wire the last 10km or so. But actually (if we think we should or not) we are not in the habit of labeling low voltage installations except those that are unusual in some way. We all expect 230 (well 200 to 250 ish measured ) relative to earth and only normally make a note when it isn't - for example 400/690  or 690/1k2. That said we have a box here with "Danger 12V" on  it which makes me chuckle. It's not even high current...

    M.

  • Well and truly off the subject.

    As @perspicuous would point out it is declared as 240-0-240 volts, so is an oddity, but common on his jobs.

     

  • Agreed, if it's 240 V nominal to Earth, then the sign is appropriate, otherwise if it's 230 V nominal to Earth then the sign  is not needed to comply with the requirements of BS 7671,.

    BUT ... if it's 230 V nominal to Earth, surely that's 460 V and not 480 V ??????