Good afternoon Team Members,
Is Terminal wiring & Feeders with LSZH ( Low Smoke Zero Halogen) insulation a requirements under BS 7671:2018 for medical locations for Group 0,1,2 as this concern sick people? Kindly help to clarify under the standard.
Good afternoon Team Members,
Is Terminal wiring & Feeders with LSZH ( Low Smoke Zero Halogen) insulation a requirements under BS 7671:2018 for medical locations for Group 0,1,2 as this concern sick people? Kindly help to clarify under the standard.
As per Andy's reply, there is no explicit wording within BS7671, nor the Department for Health Document HTM-06-01, that states the requirement for LSZH cabling within medical locations. It actually specifies that XLPE is the preferred construction type, although I would personally use LSZH.