Private network and grid connection earthing

Hi All 

I'm currently working on a project where a site is supplied via a private wire from a nearby power station unfortunately this connection has no spare capacity for the project as such we have approached the DNO for a a second connection to site one mandatory requirement they have made is that the earthing systems should be segregated, I struggle to understand how this can be achieved has anyone else been in this situation and how was it demonstrated that the earthing systems are segregated?

I have worked on sites that have two separate supplies (one from a docks ring and one from the DNO one at 11kV and one at 33kV) however we did have to  demonstrate any segregation of earthing .

Mark 

Parents
  • I agree - first question is whether the supply is LV or HV. HV in a way would be a lot easier since separating LV and HV earthing is pretty standard and you could then presumably have a common LV earthing system.

    Otherwise, does the layout of the site lend itself to being divided up into distinct and separated equipotential zones matching the two supplies?

       - Andy.

Reply
  • I agree - first question is whether the supply is LV or HV. HV in a way would be a lot easier since separating LV and HV earthing is pretty standard and you could then presumably have a common LV earthing system.

    Otherwise, does the layout of the site lend itself to being divided up into distinct and separated equipotential zones matching the two supplies?

       - Andy.