AFDD in a hospice??

Hi All,

We are currently designing a a new build extension to a children’s / young adults hospice and hoping for some guidance.

the extension will consist of 3 new bedrooms, kitchen, corridors, community room and a garden.

Firstly, we are unsure if a hospice applies to any of the buildings outlined in 421.1.7 our understanding is that is does not. So we have referred to Section 710 and referred to 710.421.1.7 and using annex A710 we have determined  the bedrooms do not require AFDD's as they are group 1  and all other rooms would fall under group 0 and require a risk assessment.

Look forward to hearing your thoughts.

 

Parents
  • Hi Everyone,

    Thanks for responses (although we slighty drifted off topic haha!)

    We have proceeded by any rooms that classify as a medical location and would cause serious harm is there AFDD was to nuisance trip we will not install (like bedrooms etc) and areas where the above does not apply like corridors we will be installing AFDD's to comply with 421.7

    Joe 

Reply
  • Hi Everyone,

    Thanks for responses (although we slighty drifted off topic haha!)

    We have proceeded by any rooms that classify as a medical location and would cause serious harm is there AFDD was to nuisance trip we will not install (like bedrooms etc) and areas where the above does not apply like corridors we will be installing AFDD's to comply with 421.7

    Joe 

Children