An interesting point made by one of my colleagues today.

If we consider a 36-way TPN distribution board that is full. How can we apply a grouping factor to those circuits at the point they leave the distribution board (the worst case position) without it making the cables so large that they can't be terminated if some of them are lighting or ring final circuits installed in trunking?

Clearly we could use sub-distribution, etc. but I have seen plenty of installations exactly like this with fairly typical 2.5sqmm or 4.0sqmm cables on the lighting and ring circuits.

Is it simply that the point of exiting the board is ignored and the main run of the cable is used for consideration of the grouping factor? If the cables are de-rated on the basis of where they come together at the board how does any installation ever practically make use of a 36-way TPN board without substantially over-sizing cables?

Parents
  • No , you don't ignore the grouping just because it's near the DB. Don't forget though, for the purposes of grouping you can ignore cables that are carrying less than 30% of their grouped rating. That should remove a significant number from the group. The second thing I would normally do with a larger DB, is to use two trunking drops, one from each side of the DB, up the wall and until the circuits split off into different directions. It usually only means a short extra length of trunking.

    regards, burn

Reply
  • No , you don't ignore the grouping just because it's near the DB. Don't forget though, for the purposes of grouping you can ignore cables that are carrying less than 30% of their grouped rating. That should remove a significant number from the group. The second thing I would normally do with a larger DB, is to use two trunking drops, one from each side of the DB, up the wall and until the circuits split off into different directions. It usually only means a short extra length of trunking.

    regards, burn

Children
    1. Yes I had overlooked the exception for <30% loaded circuits. I did suggest that a large DB like this would have circuits going in lots of different directions so it should be possible to segregate them to keep the grouping down. The trunking either side is a neat solution.