Cable grouping

An interesting point made by one of my colleagues today.

If we consider a 36-way TPN distribution board that is full. How can we apply a grouping factor to those circuits at the point they leave the distribution board (the worst case position) without it making the cables so large that they can't be terminated if some of them are lighting or ring final circuits installed in trunking?

Clearly we could use sub-distribution, etc. but I have seen plenty of installations exactly like this with fairly typical 2.5sqmm or 4.0sqmm cables on the lighting and ring circuits.

Is it simply that the point of exiting the board is ignored and the main run of the cable is used for consideration of the grouping factor? If the cables are de-rated on the basis of where they come together at the board how does any installation ever practically make use of a 36-way TPN board without substantially over-sizing cables?

Parents
  • Is it simply that the point of exiting the board is ignored

    I suspect so, although such a scenario seems a little odd for a 36-way (by which I assume that you mean 36 SP circuits/12 TP circuits) board in a commercial setting. How exactly do all the circuits leave the board - trunking, conduit, clipped direct even?

    This certainly seems to be commonly ignored in the domestic setting with a whole bunch of cables going straight back into the wall, or through the ceiling, etc.

    I doubt that this is much of a problem if it is simply that there is a very short (i.e. millimetres or a few centimetres) pinch point because of longitudinal cooling along the cables.

    Is this very different from let's say, a couple of rings and a lighting circuit squeezing through a joist in somebody's home?

  • Yes I was thinking 36 SPN ways sorry I worded it badly. I had in my mind a fairly typical commercial / office install with trunking out from the DB and wired in 'singles'.

    Completely ignored in domestics you're right. Though I think the point the others made about the incoming device limiting the amount of circuit load that can be present helps here too.

    I did once see a document from a utility company where the diversity they applied to domestic properties for the purpose of transformer sizing meant each property was based on something like a 20A supply... this may have to be revised given the EV charging sockets appearing on a lot of houses though!

  • I think that they allow a lot less than 20 A after diversity. Our consumption over the past year has been an average of 2.4 A. I wouldn't fancy the bill if it had been 20 A.

Reply Children
  • After diversity maximum demand  is a lot lower than 20A by the time that your reach the larger substation. You may find a substation with 400A fuses on each of the 3 phases and 70 or so houses on each of those phases, so not much more than  one kW each on long term average, but of course the wiring and the transformer can take 100% overload without blinking for half an hour or so, which  is good, as so can the 400A fuses...

    And yes, the DNOs will have to do some fairly serious network re-inforcement, and quite quickly, if EVs and electric heat pumps etc take off at anything near the official predicted rate.

    Mike

  • Mike, you have reminded me what I read now... forgive me it was some time ago. It was actually based on 1kW per property not 20A!