Caravan Site - Overheating supply neutral connection on pitch RCDs

Hi,

Am presently staying at a farm caravan park in south of England and the owner has shown me a problem he is having with some individual pitch electrical devices. Apparently, over time a number of the Type C  16A RCD devices have been affect by the INCOMING supply neutral connection overheating. Seems unlikely to be loose connection on so many devices and device are not tripping. 
site is served by overhead 2 phase connection with single phase distribution to at least 3 sepeate areas built at different times. Pitches are served by buried SWA and marked up as “ring”. RCDs are British supplier and all other connections on the 30mA device are clean and unaffected. Are we looking at an harmonics problem or distribution system fault. All suggestions welcome (It won’t spoil my holiday) Thanks

Dave



Parents
  • Hi DMB, probably loose connection but just a thought. Are the pitch sockets connected by actual ring final circuit? Maybe this is a bit out there, but due to the earth rods etc of the pitches there could be a potential difference between these rods/plates buried in the ground. This could make a circulating current in the ring circuit that could also make the neutral connection of the RCDs too hot. The circulating current is a current that goes around in a circle inside a circuit without going through the RCD. 

  • We have have discussed this in here previously. If the switch is 2-pole and the terminals are the same size (why would they not be) how can one run hotter than the other?

  • Let’s wait and see what DMB concludes. 

  • Remember that effective communication is a two-way street, and it’s important to listen to others’ perspectives as well as expressing your own. Instead of saying “no,” you could try saying “I disagree” or “I see things differently.” This can help keep the conversation constructive and productive. I hope this helps.

  • I hope this helps.

    No.

  • The neutral pole is many times the first suspect also on a shower pull switch if your shower draws more current than the switch can handle. What are your thoughts? 

    There have been several discussions on that very subject (and not just on overloads). Several theories abound, but my favourite is that shower pull switches (especially the types with terminals on the "faceplate") are very easy to create loose connections (as large stiff conductors, typically held by a small single screw attempt to twist as they're pushed back into the backbox) - that should happen equally with L and N of course, but then a loop test (or R1+R2) is done - so loose connections on L are much more likely to be spotted and therefore corrected; while on the other hand none of the standard tests check N continuity, so loose connections there are much more likely to go into service.

       - Andy.

  • shower pull switch

    I am asumming that it is located in the room of the shower and thus is exposed to high humidty and ingress when the shower is in operation.  What IP rating does the shower pull switch have other than a very basic IP2x ?

  • That sounds good, though how often does an R1/2 test result in a re-tightening of the terminals?  - maybe for some folk, but personally I'm struggling to think of a time. Generally it seems either pass or fail by miles because some vital part  is actually missing - being off  by fraction of an ohm is not a thing that happens to me, unless the cable length/ type is wrong.

    Mike

  • Moisture ingress wouldn't account for why (empirically) N terminals suffer more than L ones.

      - Andy.

  • Good point.  I would expect to see both terminals with the same issue.  Could that question be put to the manufacture maybe.  So someone like MK add their thoughts on why the N burns out more often than the L in a shower pull cord.  I am summing that the L and N terminals are built the same. 

  • I agree. If a terminal screw is making light contact, it will pass a loop test. It is when a current of 40 A is drawn that problems arise.

    I strongly suspect that there is observer bias going on: over-heated neutral terminals get mentioned more often and once the myth has been established, it perpetuates itself.

Reply
  • I agree. If a terminal screw is making light contact, it will pass a loop test. It is when a current of 40 A is drawn that problems arise.

    I strongly suspect that there is observer bias going on: over-heated neutral terminals get mentioned more often and once the myth has been established, it perpetuates itself.

Children
No Data