The socket rating is ok (32A, FLA of machine is 24A), but current would only be drawn on one phase
The IET is carrying out some important updates between 17-30 April and all of our websites will be view only. For more information, read this Announcement
The socket rating is ok (32A, FLA of machine is 24A), but current would only be drawn on one phase
You might equally well ask whether it is safe to supply a SP circuit from a TP DB; or what about for example, a lathe with a 3 phase motor which is not running, but a SP lamp and DRO which are.
I don't see a problem. Graham's caveat concerning RCD protection is entirely reasonable, but even then, taking one phase off a 3 phase plug isn't any different from using a BS 1363 plug in a circuit which (due to age) has no RCD protection.
Perhaps the OPs fear is the commonly held mis-belief that taking a single phase load through a three phase RCD will lead to it tripping....
Perhaps the OPs fear is the commonly held mis-belief that taking a single phase load through a three phase RCD will lead to it tripping....