The socket rating is ok (32A, FLA of machine is 24A), but current would only be drawn on one phase
The socket rating is ok (32A, FLA of machine is 24A), but current would only be drawn on one phase
What danger do you envisage might occur?
One thing to check is whether the equipment manufacturer has a specific overcurrent protective device rating (some German machines, for example, specify 25 A, which can be tricky in the UK.
And of course, if using a socket-outlet rated up to 32 A, is the outlet RCD protected in line with Regulation 411.3.3?
Thank you for the note about specific over current protective device rating.
I was wondering if there would be a danger associated with the loads being unbalanced for the 3 phase breaker supplying the socket.
That can be a rub ... in our machineshop, all the CNCs machines were connected thru 32A TPN ceeforms. This made changes easy & isolation quick and obvious. When the space was refurbished we had to remove & hardwire because of the RCD rule - try getting a 30mA RCD to hold with a CNC that contains several VFDs
That can be a rub ... in our machineshop, all the CNCs machines were connected thru 32A TPN ceeforms. This made changes easy & isolation quick and obvious. When the space was refurbished we had to remove & hardwire because of the RCD rule - try getting a 30mA RCD to hold with a CNC that contains several VFDs
As others have said, its fine. If the RCD thing is a problem and there is no local appetite for documented deviations then one can sidestep it by using a 63A socket on a supply limited by 25A MCB or whatever. Not perhaps the intention of the regs and a bit of a waste of space but not a fail either.
If you have lots of 3 phase plugs with single phase loads, it is helpful to vary the phases around so loads are not all on phase 1.. . If you like to know which phase then a stripe of tape of the phase colour on the plug serves as a reminder.
Also in the world of temporary wiring, 3 phase plugs with 3 tails emerging each with a single phase socket or strip of sockets is a common thing, although the glanding no longer meets the IP 44.
Mike