400/33kV Transformer

The transformers of 400/33kV, 160MVA & 125MVA rating should be avoided as practice of using such low MVA rating transformers are not desirable at 400kV level. It is desirable that Transformers of above ratings are only procured by utilities to have standard ratings across the country. Can anyone explain why this is?

Parents
  • Mainly standardization of parts to allow quick repairs and  maintenance procedures, and the relative costs and reach of lines of different voltage

    It mainly a matter of network design rather than technical. There is no point in running a 400KV line a short distance to power half a dozen light bulbs ;-) so 400KV stations are expensive and far apart, and serve very large areas. So given that large service area, small transformers make no sense.

    There is a similar effect at smaller scale in the LV side of things. In England we usually come down to LV from 11kV rather than 33kV, and if we have 33kV it steps down to 11kV first, though in some less densely populated areas, and in Scotland, the longer reach of a 33kV line is helpful. The fault level at 33kV is higher, the switch gear is different...

    Mike

  • Hypothetically if a large wind farm had a grid connection, with the point of connection being 400kV would there be any issues using a 400/33kV transformer to connect the wind farm to the grid? 

    I read on a paper published by the Indian government that a 400kV tx with low MVA rating is not desirable. Is there any technical issue or purely for maintenance and standardisation of assets?

Reply
  • Hypothetically if a large wind farm had a grid connection, with the point of connection being 400kV would there be any issues using a 400/33kV transformer to connect the wind farm to the grid? 

    I read on a paper published by the Indian government that a 400kV tx with low MVA rating is not desirable. Is there any technical issue or purely for maintenance and standardisation of assets?

Children
  • No, and I’m aware of proposals along those lines. There would be details to consider of course; not least as Mike says the 400kV substation cost is substantial (with timelines to boot) aand if the project is big enough to justify the cost, it’s likely to also be pushing the practical limits of the 33kV side and some intermediate voltage level may be needed due to limits on switchgear ratings etc… it’s often more attractive to go considerably further to an existing 33kV PoC.

    Oh and 400kV substations are rather large compounds, which come with the associated wider impacts and planning risks.

  • Ps I believe, but cannot substantiate, that electrified rail supplies often come from higher voltage networks than you’d expect from the demand in MVA because (in the UK at least) they’re single phase and electrically noisy and they need a strong network to minimise disturbance to other users.

    So while it mIght run at 25kV SP, the supply might be either 132kV or straight down from 400kV if the DNO can’t take it.

  • Thats really helpful, thank you.