400/33kV Transformer

The transformers of 400/33kV, 160MVA & 125MVA rating should be avoided as practice of using such low MVA rating transformers are not desirable at 400kV level. It is desirable that Transformers of above ratings are only procured by utilities to have standard ratings across the country. Can anyone explain why this is?

Parents
  • As Mike says, in the UK at least, 400kV is the supergrid - if you like the equivalent of motorways. Whereas 33kV is more like a country lane.

    Generally you don't see many country lanes connecting directly with motorways - it just adds too much complexity to the motorway system.

    Likewise a 400kV system will serve a large area and so need to be very reliable - adding lots of little connections would mean adding a lot of complexity to the 400kV system - many more points of failure, much harder to disconnect for maintenance. In general it would be better to group smaller loads together (probably via some intermediate voltage) and minimise the number of connections direct to the 400kV system.

       - Andy.

Reply
  • As Mike says, in the UK at least, 400kV is the supergrid - if you like the equivalent of motorways. Whereas 33kV is more like a country lane.

    Generally you don't see many country lanes connecting directly with motorways - it just adds too much complexity to the motorway system.

    Likewise a 400kV system will serve a large area and so need to be very reliable - adding lots of little connections would mean adding a lot of complexity to the 400kV system - many more points of failure, much harder to disconnect for maintenance. In general it would be better to group smaller loads together (probably via some intermediate voltage) and minimise the number of connections direct to the 400kV system.

       - Andy.