veterinary practices as medical locations?

How does BS 7671 define and regulate veterinary practices as medical locations? Do the electrical safety requirements for group 1 and group 2 medical locations apply to them?

Parents
  • Note 3 to 710.1 says that  Section 710 'can also be used also be used in veterinary clinics' ... although the values (of current, resistance etc.) are there to protect persons, so there's no guarantee of absolute direct transfer of requirements to all kinds of animals.

    As with designating the location as Group 0, 1 or 2 in a hospital (which is done by relevant experts in consultation with clinicians) it would be recommended to discuss the particular requirements with the veterinary professionals responsible.

  • Greetings, Graham. I value your input and expertise on this issue. I would like to hear yours and others opinions on this situation. A veterinary installation that was renovated in compliance with the chapters 11 to 61 of BS 7671, but without regard to the section 710 requirements for medical locations, has been functioning for five years without any problems. However, an EICR is required and exposes several non-conformities that do not satisfy the specific standards for group 1 or 2 locations of section 710. Would the installation be deemed unsatisfactory?

  • However, an EICR is required and exposes several non-conformities that do not satisfy the specific standards for group 1 or 2 locations of section 710. Would the installation be deemed unsatisfactory

    That is a question for the veterinary professionals involved to determine whether the practice requires any equivalents to Group 0, 1 or 0 Medical Locations ... and if there are:

    (a) Do they want you to consider it in the EICR; and

    (b) Are there any requirements (depending on what animals are being treated, in what way) that need to be put in place over and above those in Section 710 of BS 7671 ?

    This is not something that an electrician can, or should, be taking on themselves, because they do not have the veterinary medical expertise to make all the decisions, and know the issues.

    If you are being asked for an opinion, without having the relevant expertise in other veterinary surgeries, you would have to decline the work.

Reply
  • However, an EICR is required and exposes several non-conformities that do not satisfy the specific standards for group 1 or 2 locations of section 710. Would the installation be deemed unsatisfactory

    That is a question for the veterinary professionals involved to determine whether the practice requires any equivalents to Group 0, 1 or 0 Medical Locations ... and if there are:

    (a) Do they want you to consider it in the EICR; and

    (b) Are there any requirements (depending on what animals are being treated, in what way) that need to be put in place over and above those in Section 710 of BS 7671 ?

    This is not something that an electrician can, or should, be taking on themselves, because they do not have the veterinary medical expertise to make all the decisions, and know the issues.

    If you are being asked for an opinion, without having the relevant expertise in other veterinary surgeries, you would have to decline the work.