Pulling in cable - how hard can it be?

I am knackered - I have spent several hours today pulling in 3 x 16 mm² into 25 mm conduit. OSG promised me that it was possible and indeed it has been, but how difficult does it have to be?

Lube the cable, up the ladder, pull a bit, back to the beginning, lube the cable, back outside again, up the ladder, pull a bit. Down the ladder, move the ladder, up the ladder, pull a bit, down the ladder. Repeat. Repeat. Repeat.

Am I missing something?

Parents Reply Children
  • but having stripped back the T+E the bend radii of the exposed tails ought to be similar to conduit cable singles - if not then someone has been pratting with the laws of physics again ;-)

    Mike

  • but having stripped back the T+E the bend radii of the exposed tails ought to be similar to conduit cable singles - if not then someone has been pratting with the laws of physics again ;-)

    Yes, if the material and class of conductor, thickness of the insulation, and the insulating material, are the same.

    To confirm, this would be the case for 6, 10 and 16 sq mm 6192Y and 6193Y to BS 6004, compared with the same csa of H07V-R to BS EN 50525-2-31.

  • Oddly, the part reel of "extra flexible panel wire" I have, that is really pretty much the same as UK 'tri-rated' quotes a bend radius of 6 times the OD - larger than the coarser stranded stuff. But that may well be based on repeated flexing rather than one-time installation - it can certainly be bent quite  easily about a much tighter curve than that.

    Mike.