One of my old customers has deciding whether to buy a big compressor that requires a 160A  TP supply. He asked me to help him work out what is needed for the job to see if it is a worth doing. The site TNCS Ze is 0.23 so this will put the Zs above any 160A MCCB max limit. So I think we would have to go down the route of having earth fault protection on the MCCB to cover this.

My question is that as the compressor is inverter driven, am I going to be having issues with the earth fault tripping all the time?  Or is there an alternative route I should be looking at?

Parents
  • What about fitting Earthing Discs in Conducrete (its like cat litter)?

Reply
  • What about fitting Earthing Discs in Conducrete (its like cat litter)?

Children
  • What about fitting Earthing Discs in Conducrete (its like cat litter)?

    That won't reduce Ze, which for a TN-C-S or TN-S supply has to be measured to the distributor's earthing terminal, with the consumer's earthing disconnected.

  • Could they convert it to a TT system possibly?

  • That will not really make much difference - after all, you can have an RCD without having to convert to TT.

    Mike.

  • Could they convert it to a TT system possibly?

    It would be possible, (depending on whether suitable isolation is in place, taking into account that in TT systems you need to be able to isolate the Neutral for safe working).

    But it won't resolve the need for residual current fault protection, and may well cause EMC issues for VSDs.