MCCB required but Ze too high
One of my old customers has deciding whether to buy a big compressor that requires a 160A  TP supply. He asked me to help him work out what is needed for the job to see if it is a worth doing. The site TNCS Ze is 0.23 so this will put the Zs above any 160A MCCB max limit. So I think we would have to go down the route of having earth fault protection on the MCCB to cover this.
My question is that as the compressor is inverter driven, am I going to be having issues with the earth fault tripping all the time?  Or is there an alternative route I should be looking at?
  • A new transformer unless there is miles of LV wiring in the way should do rather better (substation regulation == droop at full load  at the transformer terminals is typically about 4- 5 %, i.e. if the transformer was only supplying one 200A load then  more like 0.03ohms, mostly inductive rather than winding resistance ). I presume your 0.23 ohms  (only ~ 1000 amp PSSC then)  is Zs measured at the company incomer and there is more resistace in the way to get to  the point of the new load ? (and for sanity that L-N and L-E check out the same)
    Note that 0. 2 ohms is rather more than 10m round loop path  (there and back to somewhere 5m away then) of 1mm2, or scaling to a more useful size,  350m of 35mm2  or 500m of 50mm2 etc. How far away is this upgraded transformer and how thin is the cable going to  it ? It is possible that something is a bit undersized on the DNO supply side.
    How much of the cable route is under your control ?
    M.
  • I believe the transformer is about 300m away on 185mm CNE cable. I measured that 0.23 at the cutout service head. Upgrading the cable was mentioned when the transformer was upgraded but my customer would be liable for the digging and cable costs. I think as 0.23 is still well in their max limit of 0.35 for TNCS I might be in for a hard time arguing that they need to upgrade the cable
  • 300m of 185mm2 should not be anything like that.  - 0.06 to 0.08 ohms would be more like it.
    It may be worth doing a volt drop-known load test to see if the supply impedance really is as high as you think. If it is 0.23 ohms, then a 10A kettle should dip you 2.3 volts- at the incomer, and more at the socket, you will see that on the meter.
    M.
  • That is more of the sort of figure I was expecting to see. I have inquired to Western Power to see what their readings were when they installed and commissioned the upgraded supply
  • It may be if things are a bit corroded with thin layers of oxide etc , that the low current of the tester does not punch through and make a good contact - a high current test or a load VD test may reveal better the true impedance in a  high fault current situation.
  • Yeah i agree. Th supply cable has been in there for 40+ years so thats a high possibility. I contacted Western Power this morning and they said it seemed higher than they would have expected for the site data so are sending an engineer to check it today
  • Also some loop testers aren't particularly good on very low impedance systems - some models seem better at estimating resistance than reactance, so can be thrown in situations where the reactance dominates. The phrase "fruit machine" has been used before in this context.
  • Can you apply regulation 419.3 ?
  • Tricky for an entire installation - you'd have to keep the the resistance between every pair of accessible parts (exposed- and extraneous) below 50V/Ia - for a 160A MCCB Ia might be in the region of 1250A - so R ≤ 50/1250 = 0.04Ω - you'd need some pretty fat c.pc.s/supplementary bonding conductors and probably some gold plated bonding clamps.
  • so are sending an engineer to check it today
    As they are obliged to do on request under R. 28 of ESQCR 2002.