RCD Testing Frequency

Hi All,

Where an RCD is contained within a piece of electrical equipment such as an EV charger, is it still a requirement to test the RCD every 6 months in line with BS 7671 or are the intervals now the decision of the manufacturer of the piece of equipment containing the device?

Regards

Mark

Parents
  • There are reasons why we don’t test RDC-DDs, mainly that it cannot be done correctly with an electricians installation tester



    support.myenergi.com/.../4403885493265-zappi-6mA-DC-protection-to-IEC-62955

  • Former Community Member
    0 Former Community Member in reply to Sparkingchip

    You may want to have a word with Megger and Metrel then. And yes we do test them. BS7671 states an AC test is required for verification. But if you work for an authority or a public supplying company you will prove the device operates beyond 7671 requirements to keep possibility of anything litigious at bay.  

Reply
  • Former Community Member
    0 Former Community Member in reply to Sparkingchip

    You may want to have a word with Megger and Metrel then. And yes we do test them. BS7671 states an AC test is required for verification. But if you work for an authority or a public supplying company you will prove the device operates beyond 7671 requirements to keep possibility of anything litigious at bay.  