Temp Site Supply

Hello,

I am hoping for some help/guidance from the community 

I am currently applying for a temp site supply for the construction of 6 bungalows....

I am after some guidance on what size supply i should apply for....

Thanks 

Parents
  • What loads are expected to be used ? Just power tools, a few lights and a kettle ? Or well equipped welfare facilities with electric space heating, electric cooking and electric showers.

    For the former, a single phase 60 amp supply should suffice, for the later is more likely to need 100 amp single phase.

Reply
  • What loads are expected to be used ? Just power tools, a few lights and a kettle ? Or well equipped welfare facilities with electric space heating, electric cooking and electric showers.

    For the former, a single phase 60 amp supply should suffice, for the later is more likely to need 100 amp single phase.