Temp Site Supply

Hello,

I am hoping for some help/guidance from the community 

I am currently applying for a temp site supply for the construction of 6 bungalows....

I am after some guidance on what size supply i should apply for....

Thanks 

Parents
  • Hi ARL02. My own experience of this is that the electrical supply for the temporary cabins varied depending on the project and the existing infrastructure. For a renovation project of an existing building, we provided three separate single-phase 32A supplies for the cabin, the office, and the toilet block. For a hospital extension project, we provided one three-phase 200A supply for all the cabins and shower blocks. The specification of the electrical supply was usually determined by the principle contractor who was responsible for the CDM.

Reply
  • Hi ARL02. My own experience of this is that the electrical supply for the temporary cabins varied depending on the project and the existing infrastructure. For a renovation project of an existing building, we provided three separate single-phase 32A supplies for the cabin, the office, and the toilet block. For a hospital extension project, we provided one three-phase 200A supply for all the cabins and shower blocks. The specification of the electrical supply was usually determined by the principle contractor who was responsible for the CDM.