300 mA RCD

Hi I have a problem with a 3 phase industrial ironer. main components are (3) inverters roughly 8 amps per phase (24 amps) no further details at this time.the circuit is protected with a C50 Amp MCB feeding a 300mA type B RCD. The RCD has tripped, and now will not reset even with the load disconnected and therefore requires replacement. The ironer is new. what are your thoughts?

Parents
  • Former Community Member
    Former Community Member

    Have you tried testing the RCD on ramp and without the device connected

  • I couldn’t even get it to reset. I disconnected the load cables and it stills Tripped.

  • It’s been sent back to China for tests. Despite what you all might be thinking, this is a reputable brand.

  • Former Community Member
    Former Community Member in reply to AMK

    If you cannot test it when disconnected i’d guess it’s beyond use.

  • Yep. Needs replacing. It has been suggested to bypass the RCD. I’m not ready to do this. I believe there’s a problem rather than nuisance tripping 

  • Former Community Member
    Former Community Member in reply to AMK

    How old is the circuit and why has it now started operating under no load?

  • Two weeks old. Was tested and inspected and commissioned by the manufacturer 

  • Former Community Member
    Former Community Member in reply to AMK

    At a guess, you have a NE fault or your device is at fault. Really hard to say without looking at the circuit 

Reply
  • Former Community Member
    Former Community Member in reply to AMK

    At a guess, you have a NE fault or your device is at fault. Really hard to say without looking at the circuit 