300 mA RCD

Hi I have a problem with a 3 phase industrial ironer. main components are (3) inverters roughly 8 amps per phase (24 amps) no further details at this time.the circuit is protected with a C50 Amp MCB feeding a 300mA type B RCD. The RCD has tripped, and now will not reset even with the load disconnected and therefore requires replacement. The ironer is new. what are your thoughts?

Parents
  • Former Community Member
    Former Community Member

    Have you tried testing the RCD on ramp and without the device connected

  • You can adjust the speeds at the HMI

  • Former Community Member
    Former Community Member in reply to AMK

    Its very hard to say without looking at it. If it fails under no load and the neutral is disconnected I’d go for the device. But if neutral is connected and it has loads attached i’d look at the load. I am not an expert RCDs have always been neutral issues in my previous experience 

  • Former Community Member
    Former Community Member in reply to AMK

    If you do find the fault I interested Hugging

  • It’s a machine fault that is blowing RCDs. I replaced the RCD and it ran for 4 days and now will not reset load free. I believe there a earth leakage fault >200mA. I have not considered frequency as being a problem. Having spoken with the operator that had increased the speed.

  • Former Community Member
    Former Community Member in reply to Former Community Member

    The only time I seen this happen was a three phase RCD that was three pole with single phase loads on it. Got it replaced with a four pole RCD and was okay

  • These are 4 pole RCDs

  • 3 phase. No neutral 

  • Neutral installed to the machine but not utilised 

  • Former Community Member
    Former Community Member in reply to AMK

    Theres a good document out there that shows how type b rcds are good for picking up high frequency hamonics for mode four ev chargers. They can burn out type a rcds

  • Former Community Member
    Former Community Member in reply to AMK

    Is that not ya problem? You may need a Delta RCD without neutral

Reply
  • Former Community Member
    Former Community Member in reply to AMK

    Is that not ya problem? You may need a Delta RCD without neutral