Hi I have a problem with a 3 phase industrial ironer. main components are (3) inverters roughly 8 amps per phase (24 amps) no further details at this time.the circuit is protected with a C50 Amp MCB feeding a 300mA type B RCD. The RCD has tripped, and now will not reset even with the load disconnected and therefore requires replacement. The ironer is new. what are your thoughts?

Parents
  • Can you do a PAT on the iron - i,e, strap all 3 phases and neutral and test insultion with respect to CPC or chassis at 250V DC to begin, maybe 500V later

    Any DC fault that will fire an RCD of 300mA rating should show up pretty smartly as a few thousand ohms, I imagine there is either a construction fault - pinched insulation that has now squeezed out, or there is something like a water heater element leak,

    The way you damage an RCD that quickly  is to make it break far more than its nominal rating, not a gentle trip at a a few times the nominal. Or it has been breaking and being reset far more then the user has reported.

    Mike.

  • Former Community Member
    Former Community Member in reply to mapj1

    it is operating under zero load Shrug♀️

    imbalance or neutral issue. I’m off to bed. Let me know if you sort it , I am interested Hugging

    nanight duck Hugging

Reply
  • Former Community Member
    Former Community Member in reply to mapj1

    it is operating under zero load Shrug♀️

    imbalance or neutral issue. I’m off to bed. Let me know if you sort it , I am interested Hugging

    nanight duck Hugging

Children
  • 1) your current RCD is stuffed.

    2) your Iron may (proabably does) have a problem,

    We need to try to test if these effects are independent bad luck, or as I think we both fear if  problem 2 has caused problem 1 - though it is hard to see how.

    I'd start by PA testing the iron.

    M

  • Former Community Member
    Former Community Member in reply to mapj1

    Operating with nothing connected