Hi I have a problem with a 3 phase industrial ironer. main components are (3) inverters roughly 8 amps per phase (24 amps) no further details at this time.the circuit is protected with a C50 Amp MCB feeding a 300mA type B RCD. The RCD has tripped, and now will not reset even with the load disconnected and therefore requires replacement. The ironer is new. what are your thoughts?
  • Hi Chris, the installation is a location where BE2 conditions exist. Are you asking if there’s a Three-phase voltage imbalance, not 120 degrees apart ? The 5.5 kW motor are all leaking 13.5 mA and the 1.1 kW is 7.8 mA. But you are right, it is possible that there is a somewhat intermittent fault that produces more imbalance at times, such as a loose connection, a damaged cable, or a faulty component. Is Baize used for snooker tables ? And the manufacturer specified RCD fire protection.
  • Is Baize used for snooker tables ?
    Yes indeed and for covering doors. IIRC, the cloth is trimmed during its manufacture which must produce a lot of dust.
    P.S. Strictly speaking, snooker is a game which is played on a billiard table.
    They haven't let Gregg Wallace into the factory, have they?
  • Snooker table round our way. Inside the Factory ? Did Gregg Wallace’s lack knowledge when it came to the correct terminology? Sorry the irony and sarcasm is wasted on me.
  • Oh dear!
    Gregg Wallace is a rather endearing bald greengrocer who has turned into a TV presenter.
    Neither irony nor sarcasm, but pedantry. Billiards existed long before snooker originated about 150 years ago. However, I can see its popularity, which only really started after the Beeb started showing it on the made-for-TV, Pot Black in 1969. Clearly, viewers had to be able to see the colour of the balls, whereas only the distinction of red and white was obvious in B&W (not that billiards was shown very often). Ted Lowe did his best when he said, "Steve [Davis] is going for the pink ball - and for those of you who are watching in black and white, the pink is next to the green."
  • and for those of you who are watching in black and white, the pink is next to the green."
    That has been quoted many times.  I still find it funny.
    It is almost a Michael Fish moment
    public forecasts, on any topic, which turn out to be embarrassingly wrong
    October 1987 storm