300 mA RCD
Hi I have a problem with a 3 phase industrial ironer. main components are (3) inverters roughly 8 amps per phase (24 amps) no further details at this time.the circuit is protected with a C50 Amp MCB feeding a 300mA type B RCD. The RCD has tripped, and now will not reset even with the load disconnected and therefore requires replacement. The ironer is new. what are your thoughts?
    Former Community Member in reply to mapj1
    it is operating under zero load Shrug♀️
    imbalance or neutral issue. I’m off to bed. Let me know if you sort it , I am interested Hugging
    nanight duck Hugging
  • 1) your current RCD is stuffed.
    2) your Iron may (proabably does) have a problem,
    We need to try to test if these effects are independent bad luck, or as I think we both fear if  problem 2 has caused problem 1 - though it is hard to see how.
    I'd start by PA testing the iron.
    M
    Operating with nothing connected
  • I agree if the RCD trips immediately given a good supply and nothing connected to its output terminals, then the unit is duff.
    Presumably this is an industrial environment - is there any other electrically  "noisy" equipment about? I'm just wondering about something putting large spikes on the mains - and type B RCDs will be packed with far more electronics than a traditional coil-and-solonoid AC type of yore. Any SPDs about?
  • I appreciate your feedback. I used a earth leakage clamp meter to measure the current of the seven motors that make up the machine. When I clamped all three phases (Supply) together, the current was 45 mA. When I clamped all three phases and the CPC together, the current was 390 mA (fluctuating 400 +) I measured each motor separately. The current of the three motors that were connected to inverters was around 15mA when I clamped only the phases, but it increased to around 60 mA when I clamped the CPC as well. The feeder motor, which had a power rating of 1.1kW and was supplied by an inverter, had a different current pattern. It had a low current of 7.7mA when I clamped only the phases, but a high current of 140mA when I clamped the CPC as well.
  • When I clamped all three phases (Supply) together, the current was 45 mA. When I clamped all three phases and the CPC together, the current was 390 mA (fluctuating 400 +)
    Are there any parallel earth paths from the machine (parallel to the c.p.c. that is) - e.g. any direct connections to metallic water pipes, structural steel or other machines with their own c.p.c.s. I'm just wondering if the c.p.c. currents are a bit of a red herring - either leakage originating from other parts of the installation and finding a path through your c.p.c. or even currents from outside the installations (e.g. diverted PEN currents from TN-C-S distribution systems).
    In any event RCDs just see the currents in live conductors, so clamping around just those and ignoring the c.p,c. should be sufficient to see what's happening.
  • Hello, yes. The machine has a lot of structural steel, steam pipes etc attached to it.
  • So if I can disregard the CPC readings the overall leakage current shouldn’t be a problem. I suspect I’m not being told the full story leading up-to the RCD failure. Currently I have the machine locked off, I Will reenergise tomorrow. Thanks Andy
    Then 390 mA ± 45 mA must be flowing in the CPC - this is similar to my house, but as Andy says The RCD should not care.
    If there is anything at all with the 3 phases together, where is the imbalance going? Shouldn't earth leakage through the inverters be pretty symmetrical? I wonder whether there is a somewhat intermittent fault which produces significantly more imbalance at times.
    This must be one hell of an ironer. I had imagined a commercial laundry with people and moisture, but 422.3.9 implies a textile factory. What are they making please? Baize?
  • Hi Chris, the installation is a location where BE2 conditions exist. Are you asking if there’s a Three-phase voltage imbalance, not 120 degrees apart ? The 5.5 kW motor are all leaking 13.5 mA and the 1.1 kW is 7.8 mA. But you are right, it is possible that there is a somewhat intermittent fault that produces more imbalance at times, such as a loose connection, a damaged cable, or a faulty component. Is Baize used for snooker tables ?