EICR coding for lack of local isolation of kitchen appliances

I have been asked by a friend to provide a second opinion on EICR coding for kitchen appliances connected to sockets that can only be accessed by moving the appliance, in this case the appliances are free standing and it's in rented accommodation, not HMO.

It certainly contravenes current regulation 537.3.2.

Electrician that completed the EICR is coding it as a C2 and want's to install suitable isolators with associated costs and disruption. To my mind it's a C3 as it's a bit inconvenient but the appliances can still be isolated by turning a circuit breaker of at the CU. Alternatively everything is RCD  protected, moving a free standing appliance without isolation isn't that risky.

I then started to look for documentation  and articles to provide guidance on the sittuation without much luck. Plenty describing why it's required and how to achieve it.

How would others code this, are there any articles you are aware of on the subject. When was the requirement introduced?

Appreciate any input you have. 

Parents
  • Where sockets are concealed, such as to the rear of white goods in a kitchen, separate switching should be provided in an accessible position, to allow appliances to be isolated

    But that doesn't ask for individual switching - an MCB or main switch (which is separate from the socket and appliance, and presumably is accessible) would seem to satisfy that requirement.

       - Andy.

Reply
  • Where sockets are concealed, such as to the rear of white goods in a kitchen, separate switching should be provided in an accessible position, to allow appliances to be isolated

    But that doesn't ask for individual switching - an MCB or main switch (which is separate from the socket and appliance, and presumably is accessible) would seem to satisfy that requirement.

       - Andy.